If you need assistance, please send an email to forum at 4hv dot org. To ensure your email is not marked as spam, please include the phrase "4hv help" in the subject line. You can also find assistance via IRC, at irc.shadowworld.net, room #hvcomm.
Support 4hv.org!
Donate:
4hv.org is hosted on a dedicated server. Unfortunately, this server costs and we rely on the help of site members to keep 4hv.org running. Please consider donating. We will place your name on the thanks list and you'll be helping to keep 4hv.org alive and free for everyone. Members whose names appear in red bold have donated recently. Green bold denotes those who have recently donated to keep the server carbon neutral.
Special Thanks To:
Aaron Holmes
Aaron Wheeler
Adam Horden
Alan Scrimgeour
Andre
Andrew Haynes
Anonymous000
asabase
Austin Weil
barney
Barry
Bert Hickman
Bill Kukowski
Blitzorn
Brandon Paradelas
Bruce Bowling
BubeeMike
Byong Park
Cesiumsponge
Chris F.
Chris Hooper
Corey Worthington
Derek Woodroffe
Dalus
Dan Strother
Daniel Davis
Daniel Uhrenholt
datasheetarchive
Dave Billington
Dave Marshall
David F.
Dennis Rogers
drelectrix
Dr. John Gudenas
Dr. Spark
E.TexasTesla
eastvoltresearch
Eirik Taylor
Erik Dyakov
Erlend^SE
Finn Hammer
Firebug24k
GalliumMan
Gary Peterson
George Slade
GhostNull
Gordon Mcknight
Graham Armitage
Grant
GreySoul
Henry H
IamSmooth
In memory of Leo Powning
Jacob Cash
James Howells
James Pawson
Jeff Greenfield
Jeff Thomas
Jesse Frost
Jim Mitchell
jlr134
Joe Mastroianni
John Forcina
John Oberg
John Willcutt
Jon Newcomb
klugesmith
Leslie Wright
Lutz Hoffman
Mads Barnkob
Martin King
Mats Karlsson
Matt Gibson
Matthew Guidry
mbd
Michael D'Angelo
Mikkel
mileswaldron
mister_rf
Neil Foster
Nick de Smith
Nick Soroka
nicklenorp
Nik
Norman Stanley
Patrick Coleman
Paul Brodie
Paul Jordan
Paul Montgomery
Ped
Peter Krogen
Peter Terren
PhilGood
Richard Feldman
Robert Bush
Royce Bailey
Scott Fusare
Scott Newman
smiffy
Stella
Steven Busic
Steve Conner
Steve Jones
Steve Ward
Sulaiman
Thomas Coyle
Thomas A. Wallace
Thomas W
Timo
Torch
Ulf Jonsson
vasil
Vaxian
vladi mazzilli
wastehl
Weston
William Kim
William N.
William Stehl
Wesley Venis
The aforementioned have contributed financially to the continuing triumph of 4hv.org. They are deserving of my most heartfelt thanks.
Registered Member #1412
Joined: Thu Mar 27 2008, 04:07PM
Location: Taipei Taiwan
Posts: 278
When testing my SSTC,I connected my coil to mains ground for grounding.But I got electric shock when I touch the topload of my coil.
Then I attempted measured the voltage of mains ground by holding one probe of digital multimeter by hand and use another probe to touch the mains ground.Then I get 50V reading.When using the same method to measure another line,I get 110V reading.(In the place I live the mains voltage is 110V)
Is the way I measure correct?and is it normal for me to get 50V reading on mains ground? Thanks
Registered Member #89
Joined: Thu Feb 09 2006, 02:40PM
Location: Zadar, Croatia
Posts: 3145
è¬æ˜•å“² wrote ...
When testing my SSTC,I connected my coil to mains ground for grounding.But I got electric shock when I touch the topload of my coil.
Then I attempted measured the voltage of mains ground by holding one probe of digital multimeter by hand and use another probe to touch the mains ground.Then I get 50V reading.When using the same method to measure another line,I get 110V reading.(In the place I live the mains voltage is 110V)
Is the way I measure correct?and is it normal for me to get 50V reading on mains ground? Thanks
Hello,
If you have a 3-wire grounding system, do you still get 50V when you measure between the neutral wire and ground wire? Also try connecting a light bulb in parallel with your voltmeter and see if the voltage drops to 0V. If it drops to 0V, then it's likely that your house ground got disconnected and you are getting half of your mains voltage on it (divided by caps on RFI filters!) which is a serious problem and needs to be fixed quickly. If the bolb lights at 50V, even dimly, then that's a far more serious problem that indicates a fault and/or high grounding impedance. In any case a shocking voltage on mains ground would worry me very much.
This is assuming ofcourse that the coil and no coils around it are operating at the time!
Registered Member #27
Joined: Fri Feb 03 2006, 02:20AM
Location: Hyperborea
Posts: 2058
Some countries do not have a neutral at all, step one would be to look that up for your country/region.
You are not supposed to touch the probe when measuring the mains because you are going to leave the multimeter on the wrong setting and shock yourself. The result you get will not be reliable anyway.
Grounding problems are very common so it would be no surprise if you got a problem.
Registered Member #1412
Joined: Thu Mar 27 2008, 04:07PM
Location: Taipei Taiwan
Posts: 278
Marko wrote ...
Hello,
If you have a 3-wire grounding system, do you still get 50V when you measure between the neutral wire and ground wire? Also try connecting a light bulb in parallel with your voltmeter and see if the voltage drops to 0V. If it drops to 0V, then it's likely that your house ground got disconnected and you are getting half of your mains voltage on it (divided by caps on RFI filters!) which is a serious problem and needs to be fixed quickly. If the bolb lights at 50V, even dimly, then that's a far more serious problem that indicates a fault and/or high grounding impedance. In any case a shocking voltage on mains ground would worry me very much.
This is assuming ofcourse that the coil and no coils around it are operating at the time!
Marko
I don't have a 3 wire system here.And the wiring here in Taiwan is sometimes a mess.In example,the long pin in the outlet is supposed to be neutral(according to regulations here),but in my home and many buildings it is hot.
Registered Member #89
Joined: Thu Feb 09 2006, 02:40PM
Location: Zadar, Croatia
Posts: 3145
Hi,
I don't know what the long pin in your outlet is, but if it's the only one exposed I'd guess with pretty high certainty that it's a protection pin and is supposed to be connected to ground or neutral. Have you measured the voltage between your neutral and the ground pin? My bet is that you have the third wire around several outlets, but it either came disconnected or was never connected at all in first place, and you get 50V on it from any RFI filters in power supplies that might be connected to some of outlets.
This would probably be a good time to fix your wiring - if you have no grounding system (I don't have either), you can at least assure that all your safety prongs are well connected to the neutral.
Registered Member #3610
Joined: Thu Jan 13 2011, 03:29AM
Location: Seattle, WA
Posts: 506
è¬æ˜•å“² wrote ...
Marko wrote ...
Hello,
If you have a 3-wire grounding system, do you still get 50V when you measure between the neutral wire and ground wire? Also try connecting a light bulb in parallel with your voltmeter and see if the voltage drops to 0V. If it drops to 0V, then it's likely that your house ground got disconnected and you are getting half of your mains voltage on it (divided by caps on RFI filters!) which is a serious problem and needs to be fixed quickly. If the bolb lights at 50V, even dimly, then that's a far more serious problem that indicates a fault and/or high grounding impedance. In any case a shocking voltage on mains ground would worry me very much.
This is assuming ofcourse that the coil and no coils around it are operating at the time!
Marko
I don't have a 3 wire system here.And the wiring here in Taiwan is sometimes a mess.In example,the long pin in the outlet is supposed to be neutral(according to regulations here),but in my home and many buildings it is hot.
This sort of thing is all too common even in areas that are fairly well regulated. Over the years homeowners with just enough knowledge to be dangerous add/change parts of the system and you can have a dangerous situation. When I bought my house, the whole basement had been wired and finished by the original owner. I found that every switch he installed was on the neutral rather than hot, there was at least one receptacle wired backwards, and the wires had been trimmed back so short that they ripped out of the back of many of the receptacles when I removed them and I had to splice in pigtails to connect the new ones.
If you are playing with high voltage, I strongly recommend you properly wire the receptacle you use for these things, if only that one. If there is no earth ground available, put a clamp on a nearby cold water pipe or drive a rod into the ground and bring that in somewhere to ground your HV apparatus. Whatever you ground to, *verify* that it is actually earthed. The fun stuff is dangerous enough already without needlessly adding further risk.
Registered Member #1412
Joined: Thu Mar 27 2008, 04:07PM
Location: Taipei Taiwan
Posts: 278
James wrote ...
[This sort of thing is all too common even in areas that are fairly well regulated. Over the years homeowners with just enough knowledge to be dangerous add/change parts of the system and you can have a dangerous situation. When I bought my house, the whole basement had been wired and finished by the original owner. I found that every switch he installed was on the neutral rather than hot, there was at least one receptacle wired backwards, and the wires had been trimmed back so short that they ripped out of the back of many of the receptacles when I removed them and I had to splice in pigtails to connect the new ones.
If you are playing with high voltage, I strongly recommend you properly wire the receptacle you use for these things, if only that one. If there is no earth ground available, put a clamp on a nearby cold water pipe or drive a rod into the ground and bring that in somewhere to ground your HV apparatus. Whatever you ground to, *verify* that it is actually earthed. The fun stuff is dangerous enough already without needlessly adding further risk.
I live in a tall building so putting a rod to ground is impossible for me. Why cold water pipe can work?Will this work in a tall buildings?
Registered Member #3610
Joined: Thu Jan 13 2011, 03:29AM
Location: Seattle, WA
Posts: 506
è¬æ˜•å“² wrote ...
James wrote ...
[This sort of thing is all too common even in areas that are fairly well regulated. Over the years homeowners with just enough knowledge to be dangerous add/change parts of the system and you can have a dangerous situation. When I bought my house, the whole basement had been wired and finished by the original owner. I found that every switch he installed was on the neutral rather than hot, there was at least one receptacle wired backwards, and the wires had been trimmed back so short that they ripped out of the back of many of the receptacles when I removed them and I had to splice in pigtails to connect the new ones.
If you are playing with high voltage, I strongly recommend you properly wire the receptacle you use for these things, if only that one. If there is no earth ground available, put a clamp on a nearby cold water pipe or drive a rod into the ground and bring that in somewhere to ground your HV apparatus. Whatever you ground to, *verify* that it is actually earthed. The fun stuff is dangerous enough already without needlessly adding further risk.
I live in a tall building so putting a rod to ground is impossible for me. Why cold water pipe can work?Will this work in a tall buildings?
Traditionally water pipes feeding homes were metal and ran through the ground, so early grounding systems used the cold water pipe as a ground rod. The hot water pipe runs through the water heater and may be isolated there. Of course now plastic is often used for water mains so this may not work, and in Taiwan I have NO idea how things are done, so I can't say whether this will work. If in doubt, test it. A light bulb connected between hot and a good ground connection should light to normal brightness.
This site is powered by e107, which is released under the GNU GPL License. All work on this site, except where otherwise noted, is licensed under a Creative Commons Attribution-ShareAlike 2.5 License. By submitting any information to this site, you agree that anything submitted will be so licensed. Please read our Disclaimer and Policies page for information on your rights and responsibilities regarding this site.