effect of sudden loss of reactive power supply for an induction generator
scrooch
Sun Jan 30 2011, 01:09AM Print
scrooch Registered Member #908 Joined: Wed Jul 18 2007, 05:53AM
So im having this problem at work where a 150kW induction motor is being used as an induction generator. There is a capacitor bank in parallel to the induction generator which is primarily for PFC(the reactive power requirement of the generator is fed by the grid).
Assume the induction generator is islanded( i.e the capacitor bank is out, the grid is out and the induction generator is the only thing that's connected to the load)
What would happen to the induction generators speed?
If a step by step explanation on what will happen would be great.
From my thinking when the capacitor bank and the grid power goes out the generator has no source of vars to sustain the stator magnetic fields.
(i.e stator magnetic field will collapse pretty much instantly which will produce a large voltage in the stator coils due to Ldi/dt)
1)After this initial Ldi/dt voltage spike it would cause a large current to flow in the stator coils?and it would oscillate?
2)Or because of the lack of reactive power the stator will have no magnetic field and that would stop inducing and emf on the rotor which will collapse the rotor magnetic field and stop the generator all together?
say the magentic field is not there anymore in the stator, would it cause the rotor(which is connected to an impeller) to freewheel and destruct itself?
radiotech
Sun Jan 30 2011, 02:30AM
You are correct as to the spinup destruction. The oscillation,
will occur but the spark across the contactor between the generator and the grid will eat that energy, Is this 1 200 HP 600 volt machine?
Motor insulation is tested in certain cases by hitting the the
winding with a fast rising pulse and looking at the ringing
the coils produce with their self-capacity.
Iy you dont do it correctly, you will restroy the insulation,
leaving no doubts about its quality.
scrooch
Sun Jan 30 2011, 02:37AM
this is a 150kW machine 415v machine delta connected
Sun Jan 30 2011, 09:22AM
If the generator loses its capacitor bank, it can't generate any more. An induction generator needs a capacitive load to excite it. The rotor will demagnetise, the output voltage collapse to zero, and it will stop consuming mechanical power, which may make the prime mover run away.
If it gets islanded with a load that's unity or leading power factor, it could keep on generating, with voltage and frequency way out of spec. So you probably want to make sure that the load it's islanded with is not PFCd.
You can get regulators for induction generators, intended for the micro-hydro industry, if you can call it an industry.
scrooch
Sun Jan 30 2011, 10:25AM
Steve McConner wrote ...
what do you think would happen in the instant the capacitor bank is out?
would the voltage instantaneously rise at that very moment due to the collapsing field?
Frosty90
Tue Feb 01 2011, 09:27AM
Frosty90 Registered Member #1617 Joined: Fri Aug 01 2008, 07:31AM
If it was connected to a unity power factor load, and not to the grid I'd think the voltage would go through the basement, rather than up, since there'd be no more excitation from the caps?
Tue Feb 01 2011, 09:44AM
scrooch wrote ...
I don't know. It might do, but I think the spike would be no bigger than what you got when switching out a 150kVA transformer.
If it's really critical, you should simulate the system using something like EMTP. Link2
scrooch
Tue Feb 01 2011, 10:49AM
thanks for your help, i will look at the transient analysis program