Welcome
Username or Email:

Password:


Missing Code




[ ]
[ ]
Online
  • Guests: 19
  • Members: 0
  • Newest Member: omjtest
  • Most ever online: 396
    Guests: 396, Members: 0 on 12 Jan : 12:51
Members Birthdays:
One birthday today, congrats!
Danielle (34)


Next birthdays
07/07 MicroTesla (34)
07/09 Avi (41)
07/09 Jannick Hagen (15)
Contact
If you need assistance, please send an email to forum at 4hv dot org. To ensure your email is not marked as spam, please include the phrase "4hv help" in the subject line. You can also find assistance via IRC, at irc.shadowworld.net, room #hvcomm.
Support 4hv.org!
Donate:
4hv.org is hosted on a dedicated server. Unfortunately, this server costs and we rely on the help of site members to keep 4hv.org running. Please consider donating. We will place your name on the thanks list and you'll be helping to keep 4hv.org alive and free for everyone. Members whose names appear in red bold have donated recently. Green bold denotes those who have recently donated to keep the server carbon neutral.


Special Thanks To:
  • Aaron Holmes
  • Aaron Wheeler
  • Adam Horden
  • Alan Scrimgeour
  • Andre
  • Andrew Haynes
  • Anonymous000
  • asabase
  • Austin Weil
  • barney
  • Barry
  • Bert Hickman
  • Bill Kukowski
  • Blitzorn
  • Brandon Paradelas
  • Bruce Bowling
  • BubeeMike
  • Byong Park
  • Cesiumsponge
  • Chris F.
  • Chris Hooper
  • Corey Worthington
  • Derek Woodroffe
  • Dalus
  • Dan Strother
  • Daniel Davis
  • Daniel Uhrenholt
  • datasheetarchive
  • Dave Billington
  • Dave Marshall
  • David F.
  • Dennis Rogers
  • drelectrix
  • Dr. John Gudenas
  • Dr. Spark
  • E.TexasTesla
  • eastvoltresearch
  • Eirik Taylor
  • Erik Dyakov
  • Erlend^SE
  • Finn Hammer
  • Firebug24k
  • GalliumMan
  • Gary Peterson
  • George Slade
  • GhostNull
  • Gordon Mcknight
  • Graham Armitage
  • Grant
  • GreySoul
  • Henry H
  • IamSmooth
  • In memory of Leo Powning
  • Jacob Cash
  • James Howells
  • James Pawson
  • Jeff Greenfield
  • Jeff Thomas
  • Jesse Frost
  • Jim Mitchell
  • jlr134
  • Joe Mastroianni
  • John Forcina
  • John Oberg
  • John Willcutt
  • Jon Newcomb
  • klugesmith
  • Leslie Wright
  • Lutz Hoffman
  • Mads Barnkob
  • Martin King
  • Mats Karlsson
  • Matt Gibson
  • Matthew Guidry
  • mbd
  • Michael D'Angelo
  • Mikkel
  • mileswaldron
  • mister_rf
  • Neil Foster
  • Nick de Smith
  • Nick Soroka
  • nicklenorp
  • Nik
  • Norman Stanley
  • Patrick Coleman
  • Paul Brodie
  • Paul Jordan
  • Paul Montgomery
  • Ped
  • Peter Krogen
  • Peter Terren
  • PhilGood
  • Richard Feldman
  • Robert Bush
  • Royce Bailey
  • Scott Fusare
  • Scott Newman
  • smiffy
  • Stella
  • Steven Busic
  • Steve Conner
  • Steve Jones
  • Steve Ward
  • Sulaiman
  • Thomas Coyle
  • Thomas A. Wallace
  • Thomas W
  • Timo
  • Torch
  • Ulf Jonsson
  • vasil
  • Vaxian
  • vladi mazzilli
  • wastehl
  • Weston
  • William Kim
  • William N.
  • William Stehl
  • Wesley Venis
The aforementioned have contributed financially to the continuing triumph of 4hv.org. They are deserving of my most heartfelt thanks.
Forums
4hv.org :: Forums :: High Voltage
« Previous topic | Next topic »   

My new PT: 14.4kV Westinghouse

 1 2 3 
Move Thread LAN_403
sparky
Thu Jul 26 2007, 07:46AM
sparky Registered Member #530 Joined: Sat Feb 17 2007, 07:56AM
Location: Victoria BC, Canada
Posts: 178
Well, I got the 120V rated transformer interfacing a 240V 30A dryer outlet for the time being. i'm using another lower voltage PT in series on the primary side for extra windings so I can pass 240V without saturation. I'm using 200 ft worth of stranded 10AWG on a mid sized transformer core for inductive load ballsting. This provides some ballasting - seems to allow up to 36A average and the wire gets slightly warm... I might upgrade to a 40A range outlet...
1185435961 530 FT27570 Dscn0834
Back to top
kv
Thu Jul 26 2007, 09:48AM
kv Registered Member #809 Joined: Wed May 30 2007, 08:59AM
Location: Melbourne, victoria
Posts: 114
cool!!! they are big arcs!!so your using your dryer outlet amazed i want one!! any more pics, vids?
Back to top
J. Aaron Holmes
Thu Jul 26 2007, 03:58PM
J. Aaron Holmes Registered Member #477 Joined: Tue Jun 20 2006, 11:51PM
Location: Seattle, WA
Posts: 546
sparky wrote ...

Well, I got the 120V rated transformer interfacing a 240V 30A dryer outlet for the time being. i'm using another lower voltage PT in series on the primary side for extra windings so I can pass 240V without saturation.

Nice arc! 8.5+kVA from a 1.75kVA tranny is definitely pushing things! cheesey

Putting transformer primaries in series to avoid overvoltage is fraught with peril. Your little PT probably won't pass more than 1A without the secondary shorted, so I assume that's what you've done. Realize then that the inductance of the primary becomes minescule. When you're not drawing an arc from the big PT, the total impedance of the ballast + little PT + big PT arrangement is then hugely dominated by the inductance of the big PT's primary, causing it to see ~240V. Have you measured it? Really, I expect the smaller PT is doing almost nothing to limit the voltage to the big PT, but rather is acting simply as part of the ballast, and that you'd accomplish the same thing by adding more turns to your ballast and getting rid of the smaller PT.

EDIT: And BTW, though I don't doubt a PT or pig can run at 2x rated voltage for some time (I have tried it), you may be seriously challenging your transformer's insulation, especially if you run a TC and subject it to 2x voltage plus the resonant rise, spikes, etc. that come out of a TC primary circuit. My friend destroyed a very large pole pig that way! Many people who have experience only with smaller transformers like to say that putting 240V into the 120V windings of a pig will lead to saturation, and that you won't get 2x the HV out. Which, as far as I can tell, is baloney with these big units.

Cheers,
Aaron, N7OE
Back to top
sparky
Fri Jul 27 2007, 12:48AM
sparky Registered Member #530 Joined: Sat Feb 17 2007, 07:56AM
Location: Victoria BC, Canada
Posts: 178
Actually yeah, I did do some measurements on the primary of my large PT. It reads 118.5 V --- voltage can be 121.2 V but well within standard operating range. I've never had more than this on the primary.

The smaller PT isn't shorted and is left without a load.
All the ballasting is coming from the green wire wrapped transformer core.... I think I might need more wire -- only 200ft worth so far... I'm averaging 35A load.

Here is a video clip... enjoy.
]1185497326_530_FT27570_dscn0834.avi[/file]
Back to top
J. Aaron Holmes
Fri Jul 27 2007, 02:16AM
J. Aaron Holmes Registered Member #477 Joined: Tue Jun 20 2006, 11:51PM
Location: Seattle, WA
Posts: 546
sparky wrote ...

Actually yeah, I did do some measurements on the primary of my large PT. It reads 118.5 V. The smaller PT isn't shorted and is left without load. All the ballasting is coming from the green wire wrapped transformer core.... I think I might need more wire -- only 200ft worth so far... I'm averaging 35A load.

Here is a video clip... enjoy.


Your small PT *isn't* shorted, and is passing 30+A!?!?!?! suprised Believe me; that ain't good! So your small PT must be seriously saturated or arcing internally. That is the only explanation. If neither of these conditions exist, then your PT would pass < 1A. I'm assuming, then, that you measured the 118.5V when you were *not* drawing an arc. If you drew an arc, the voltage across the big PT would plummet and the voltage across the small PT would soar to ~240V. This is probably causing your small PT to saturate, under which condition it might easily pass 30+A. Don't fry your new toys! angry

Even under no load, you are very fortunate if the voltage on your big PT is such a nice 1/2 of the 240V supplied.

Cheers,
Aaron, N7OE
Back to top
sparky
Fri Jul 27 2007, 03:15AM
sparky Registered Member #530 Joined: Sat Feb 17 2007, 07:56AM
Location: Victoria BC, Canada
Posts: 178
The voltage drops down to 90 V when arced - then again so do my neons too...

What do you suggest I do Aaron? What the best way to run this set up using a balanced system without investing in another PT?
Back to top
J. Aaron Holmes
Fri Jul 27 2007, 04:02AM
J. Aaron Holmes Registered Member #477 Joined: Tue Jun 20 2006, 11:51PM
Location: Seattle, WA
Posts: 546
sparky wrote ...

The voltage drops down to 90 V when arced - then again so do my neons too...

What do you suggest I do Aaron? What the best way to run this set up using a balanced system without investing in another PT?

It would be interesting to scope it. There is probably some serious non-sinusoidal action going on.

Well, as far as not investing in another PT, how about in a 30+A 120V socket? Might only cost you $20-30 in parts/wire. Do you have access to the breaker box? A dedicated "geek socket" like this is always best, IMO. This also helps a bit with RF polution in the rest of your house wiring (if you're building a TC), since otherwise any RF getting into the mains ground gets to take the "long way", which may send it past some high-$$ computer and stereo gear angry.

Another possibility is that your dryer socket has a neutral lead. Does it? Some do, some don't.

Getting more PTs is certainly good!! wink But I'm always a bit shy of anything that involves putting primaries in series where that connection is left to float. You're just asking for trouble, because who knows where that connection will float off to when the loads on the transformers are not balanced? If the outputs are placed in series or parallel, you're definitely better off, but... Instead of getting another PT, you might just look out for a 120/240V transformer. It doesn't have to be a transformer made for turning 240V into 120V. It could be a 480V transformer with 120/240V secondary, for example. In this latter case, you can just leave the e.g., 480V winding disconnected, and use the 120/240V secondary as an autotransformer. Or get a variac; same idea. But high-current 240V variacs can command a hefty price tag!

For my own HV geekery, I installed a four-prong 50A electric range socket next to my breaker box in the garage. That lets me have 50A 240V or 120V. The heads are a little expensive when new from the store, but that's what junky surplus stores are for; I got 5 used ones for $5 from Pacific Industrial in Seattle last year. That was before they moved, though, and now I'm told they're way less junky cry cry

Cheers,
Aaron, N7OE
Back to top
Steve Conner
Fri Jul 27 2007, 08:56AM
Steve Conner Registered Member #30 Joined: Fri Feb 03 2006, 10:52AM
Location: Glasgow, Scotland
Posts: 6706
The smaller PT will be acting like a saturable reactor. I expect it has much the same effect on the waveform as a triac lamp dimmer turned to about halfway. If I were you I'd ditch it and just put more turns on your ballast choke.
Back to top
sparky
Fri Jul 27 2007, 01:43PM
sparky Registered Member #530 Joined: Sat Feb 17 2007, 07:56AM
Location: Victoria BC, Canada
Posts: 178
UPDATE:

I do have a double pole single throw breaker and wire job - 4 wire to be exact. The demonstration area I have lined up for October only have a single 240V 60A 3 wire connection.... so I'm going to be investing in something in another transformer anyways...and run both in sets of primaries in series and secondaries in parallel. Maybe - just maybe I can put a breaker box in for 120V 60A and run it close to the transformer with RF protection gear and an on -off switch. That would be good.

My target is power is 5500 watts...
Back to top
J. Aaron Holmes
Fri Jul 27 2007, 04:25PM
J. Aaron Holmes Registered Member #477 Joined: Tue Jun 20 2006, 11:51PM
Location: Seattle, WA
Posts: 546
Steve Conner wrote ...

The smaller PT will be acting like a saturable reactor. I expect it has much the same effect on the waveform as a triac lamp dimmer turned to about halfway. If I were you I'd ditch it and just put more turns on your ballast choke.
But regardless of keeping the small PT or putting more turns on the ballast, a PT somewhere is going to be seeing 240V at various points, right? That doesn't seem especially nice. At least not if you're *also* going to be "mean" to the PT(s) by using it/them for a TC.

sparky wrote ...

I do have a double pole single throw breaker and wire job - 4 wire to be exact. The demonstration area I have lined up for October only have a single 240V 60A 3 wire connection.... so I'm going to be investing in something in another transformer anyways...and run both in sets of primaries in series and secondaries in parallel. Maybe - just maybe I can put a breaker box in for 120V 60A and run it close to the transformer with RF protection gear and an on -off switch. That would be good.
I see. The series/parallel thing should work ok. Also, you might just check with a local tool rental place and see if they rent out tool transformers. Or you could rent a generator.

Cheers,
Aaron, N7OE
Back to top
 1 2 3 

Moderator(s): Chris Russell, Noelle, Alex, Tesladownunder, Dave Marshall, Dave Billington, Bjørn, Steve Conner, Wolfram, Kizmo, Mads Barnkob

Go to:

Powered by e107 Forum System
 
Legal Information
This site is powered by e107, which is released under the GNU GPL License. All work on this site, except where otherwise noted, is licensed under a Creative Commons Attribution-ShareAlike 2.5 License. By submitting any information to this site, you agree that anything submitted will be so licensed. Please read our Disclaimer and Policies page for information on your rights and responsibilities regarding this site.