If you need assistance, please send an email to forum at 4hv dot org. To ensure your email is not marked as spam, please include the phrase "4hv help" in the subject line. You can also find assistance via IRC, at irc.shadowworld.net, room #hvcomm.
Support 4hv.org!
Donate:
4hv.org is hosted on a dedicated server. Unfortunately, this server costs and we rely on the help of site members to keep 4hv.org running. Please consider donating. We will place your name on the thanks list and you'll be helping to keep 4hv.org alive and free for everyone. Members whose names appear in red bold have donated recently. Green bold denotes those who have recently donated to keep the server carbon neutral.
Special Thanks To:
Aaron Holmes
Aaron Wheeler
Adam Horden
Alan Scrimgeour
Andre
Andrew Haynes
Anonymous000
asabase
Austin Weil
barney
Barry
Bert Hickman
Bill Kukowski
Blitzorn
Brandon Paradelas
Bruce Bowling
BubeeMike
Byong Park
Cesiumsponge
Chris F.
Chris Hooper
Corey Worthington
Derek Woodroffe
Dalus
Dan Strother
Daniel Davis
Daniel Uhrenholt
datasheetarchive
Dave Billington
Dave Marshall
David F.
Dennis Rogers
drelectrix
Dr. John Gudenas
Dr. Spark
E.TexasTesla
eastvoltresearch
Eirik Taylor
Erik Dyakov
Erlend^SE
Finn Hammer
Firebug24k
GalliumMan
Gary Peterson
George Slade
GhostNull
Gordon Mcknight
Graham Armitage
Grant
GreySoul
Henry H
IamSmooth
In memory of Leo Powning
Jacob Cash
James Howells
James Pawson
Jeff Greenfield
Jeff Thomas
Jesse Frost
Jim Mitchell
jlr134
Joe Mastroianni
John Forcina
John Oberg
John Willcutt
Jon Newcomb
klugesmith
Leslie Wright
Lutz Hoffman
Mads Barnkob
Martin King
Mats Karlsson
Matt Gibson
Matthew Guidry
mbd
Michael D'Angelo
Mikkel
mileswaldron
mister_rf
Neil Foster
Nick de Smith
Nick Soroka
nicklenorp
Nik
Norman Stanley
Patrick Coleman
Paul Brodie
Paul Jordan
Paul Montgomery
Ped
Peter Krogen
Peter Terren
PhilGood
Richard Feldman
Robert Bush
Royce Bailey
Scott Fusare
Scott Newman
smiffy
Stella
Steven Busic
Steve Conner
Steve Jones
Steve Ward
Sulaiman
Thomas Coyle
Thomas A. Wallace
Thomas W
Timo
Torch
Ulf Jonsson
vasil
Vaxian
vladi mazzilli
wastehl
Weston
William Kim
William N.
William Stehl
Wesley Venis
The aforementioned have contributed financially to the continuing triumph of 4hv.org. They are deserving of my most heartfelt thanks.
for the mill I am making, the spindle motor I found is a 24V at 150+Amps. So naturally the problem is providing that power. I've found a pre-wound 5kVa 3 phase transformer - but for around 100V output voltage. The secondary will be rewound for the needed voltage/amperage.
The primary is connected in star configuration, the center will be grounded. The question is how to wind the secondary - in delta or in star. I will be using a 3 phase rectifier after that and around 60mF capacitance.
If it is configured in Delta - the current in each of the secondary will decrease (but more windings will be needed). Also the 3rd harmonic is suppressed better. So I think it is the better choice.
Am I missing something fundamental here ? 3 phase is mister for me. Is the star connection better in any way for this application ?
Registered Member #72
Joined: Thu Feb 09 2006, 08:29AM
Location: UK St. Albans
Posts: 1659
Star will allow you fewer turns on the secondary for the same output voltage after the rectifier, so may be easier to wind. However you will be using fat wire so this advantage may be moot. The cente-tap used in the star config allows you an easier analysis of how your bridge recitifier is working, so that's the 'obvious' one to go for. It also allows you to use the phases unbalanced for other things, like powering some electronics, again the simpler choice to make. If you connect three star windings wrongly, the load doesn't see the full voltage. If you connect three delta windings wrongly, the transformer smokes. I think star is winning 3-0.
You can be clever in several ways. a) Configure your 3 windings in delta OR star switchable to give you root(3) difference in output voltage. b) Wind a delta set AND a star set, and use a 3 phase bridge rectifier on both. With the right ratio of windings, you have a '12 pulse' recitifier which gives you very little ripple, rather than the '6 pulse' rectifier using one set alone (ordinary single phase gives you a 2 pulse recitifier for comparison). Lower ripple means less heating in your motor, slightly, the difference may not be worth having. See wikipedia rectifiers.
Don't worry too much about harmonic distortion, unless you are selling equipment to a spec. Both delta, and star with no connection to the star point, refuse to allow 3rd and 3N harmonic currents to flow. It's only an issue when a supplier puts a flimsy neutral connection in, as it will carry 'little current' when the balanced load currents subtract in the neutral, and then sees it overheat when all the loads draw a large 3rd harmonic current waveform which adds in the neutral conductor.
Thank you for your helpful reply. I liked the point with "no smoke"
Making multiple sets of winding is a bit too much, but I definitely liked this one:
Dr. Slack wrote ...
b) Wind a delta set AND a star set, and use a 3 phase bridge rectifier on both. With the right ratio of windings, you have a '12 pulse' recitifier which gives you very little ripple, rather than the '6 pulse' rectifier using one set alone.
I guess this is due to the 30 degree phase shift when you have a star-delta configuration ?
Dr. Slack wrote ...
Both delta, and star with no connection to the star point, refuse to allow 3rd and 3N harmonic currents to flow. It's only an issue when a supplier puts a flimsy neutral connection in, as it will carry 'little current' when the balanced load currents subtract in the neutral, and then sees it overheat when all the loads draw a large 3rd harmonic current waveform which adds in the neutral conductor.
I couldn't understand the above - so not to have a 3rd harmonic you need to use a thick neutral wire or leave it floating ?!
I was planning to connect the center of the primary star to neutral, and was wondering what to do with the secondary star center ?
Registered Member #72
Joined: Thu Feb 09 2006, 08:29AM
Location: UK St. Albans
Posts: 1659
Dr. H. wrote ...
Dr. Slack wrote ...
Both delta, and star with no connection to the star point, refuse to allow 3rd and 3N harmonic currents to flow. It's only an issue when a supplier puts a flimsy neutral connection in, as it will carry 'little current' when the balanced load currents subtract in the neutral, and then sees it overheat when all the loads draw a large 3rd harmonic current waveform which adds in the neutral conductor.
I couldn't understand the above - so not to have a 3rd harmonic you need to use a thick neutral wire or leave it floating ?!
I was planning to connect the center of the primary star to neutral, and was wondering what to do with the secondary star center ?
Cheers
*You* don't have a problem with 3rd harmonic, the supply company does. If you, and the rest of the district, throw too much back at them, then their neutrals could overheat, if the neutrals are sized assuming a reasonable degree of phase balance. So you can pretty much forget about 3rd harmonic as a domestic user. Because it causes the supply company problems, there is often a limit on how much 3rd harmonic commerically sold equipment is allowed to fling back. That's why power factor correction electronics is becoming more prevalent, it's mandatory on loads above, I think, 300W, in many jurisctictions. A capacitor input rectifier, because it only conducts at the peak of the waveform, is good at causing bad 3rd harmonic.
If you don't sell stuff, then who's going to know? Your few amps of 3rd is not going to embarass any supply transformers. You might, out of the goodness of your heart, put a bit of inductance in the phases to improve the power factor by increasing the conduction angle. However, that improves high harmonics first, you need a lot of inductance to make any improvement in 3rd, so it's not really worth it.
You connect the secondary star to (a) the approrpiate point on your output caps. If, as is typical, you generate +/- supplies and have 6 caps, 3+ve, 3-ve, then the neutral star connects to the centre tap of these, the 0v connection . Then, (b) you need to decide what secondary earthing practice you use, where you connect your output 0v to. The transformer provides isolation. You could leave 0v floating, or you could connect it to a ground spike, or to mains earth. All three have their merits, it depends on the particular circumstances which is best to use.
Registered Member #72
Joined: Thu Feb 09 2006, 08:29AM
Location: UK St. Albans
Posts: 1659
It occurs to me that perhaps I have over-sold the star to 0v configuration. There is quite a lot of ripple on each of the +ve and -ve, each is fed by a 3-pulse rectifier. However, these pulses are anti-phased, and the differential output from +ve to -ve has the much lower 6 pulse ripple.
So the avilability of the centre tap is more of a convenience for other circuitry.
The biggest advantage of the Delta configuration is that the phase current decreases (Iph = I(line)/sqrt(3) .... so this is quite a lot for this application
Registered Member #72
Joined: Thu Feb 09 2006, 08:29AM
Location: UK St. Albans
Posts: 1659
Dr. H. wrote ...
The biggest advantage of the Delta configuration is that the phase current decreases (Iph = I(line)/sqrt(3) .... so this is quite a lot for this application
I'm not sure I understand what you're asserting here? You would not be saying that like for like, for the same line input voltage, and rectifier output power, that the delta configuration achieves a factor of 1.732 lower current consumption. That would mean such a collossal difference in efficiency that star would never be used. So it must be something else.
Registered Member #11591
Joined: Wed Mar 20 2013, 08:20PM
Location: UK
Posts: 556
Dr. Slack wrote ...
Dr. H. wrote ...
The biggest advantage of the Delta configuration is that the phase current decreases (Iph = I(line)/sqrt(3) .... so this is quite a lot for this application
I'm not sure I understand what you're asserting here? You would not be saying that like for like, for the same line input voltage, and rectifier output power, that the delta configuration achieves a factor of 1.732 lower current consumption. That would mean such a collossal difference in efficiency that star would never be used. So it must be something else.
In star, the windings are put two in series phase to phase with 0V in the middle. In delta, only one winding goes between the phases, and so has a greater volts per turn and greater voltage. If the voltage increases, the current decreases, to the extent that Dr. H described.
This site is powered by e107, which is released under the GNU GPL License. All work on this site, except where otherwise noted, is licensed under a Creative Commons Attribution-ShareAlike 2.5 License. By submitting any information to this site, you agree that anything submitted will be so licensed. Please read our Disclaimer and Policies page for information on your rights and responsibilities regarding this site.