Welcome
Username or Email:

Password:


Missing Code




[ ]
[ ]
Online
  • Guests: 40
  • Members: 0
  • Newest Member: omjtest
  • Most ever online: 396
    Guests: 396, Members: 0 on 12 Jan : 12:51
Members Birthdays:
No birthdays today

Next birthdays
07/09 Avi (41)
07/09 Jannick Hagen (15)
07/10 Sparcz (69)
Contact
If you need assistance, please send an email to forum at 4hv dot org. To ensure your email is not marked as spam, please include the phrase "4hv help" in the subject line. You can also find assistance via IRC, at irc.shadowworld.net, room #hvcomm.
Support 4hv.org!
Donate:
4hv.org is hosted on a dedicated server. Unfortunately, this server costs and we rely on the help of site members to keep 4hv.org running. Please consider donating. We will place your name on the thanks list and you'll be helping to keep 4hv.org alive and free for everyone. Members whose names appear in red bold have donated recently. Green bold denotes those who have recently donated to keep the server carbon neutral.


Special Thanks To:
  • Aaron Holmes
  • Aaron Wheeler
  • Adam Horden
  • Alan Scrimgeour
  • Andre
  • Andrew Haynes
  • Anonymous000
  • asabase
  • Austin Weil
  • barney
  • Barry
  • Bert Hickman
  • Bill Kukowski
  • Blitzorn
  • Brandon Paradelas
  • Bruce Bowling
  • BubeeMike
  • Byong Park
  • Cesiumsponge
  • Chris F.
  • Chris Hooper
  • Corey Worthington
  • Derek Woodroffe
  • Dalus
  • Dan Strother
  • Daniel Davis
  • Daniel Uhrenholt
  • datasheetarchive
  • Dave Billington
  • Dave Marshall
  • David F.
  • Dennis Rogers
  • drelectrix
  • Dr. John Gudenas
  • Dr. Spark
  • E.TexasTesla
  • eastvoltresearch
  • Eirik Taylor
  • Erik Dyakov
  • Erlend^SE
  • Finn Hammer
  • Firebug24k
  • GalliumMan
  • Gary Peterson
  • George Slade
  • GhostNull
  • Gordon Mcknight
  • Graham Armitage
  • Grant
  • GreySoul
  • Henry H
  • IamSmooth
  • In memory of Leo Powning
  • Jacob Cash
  • James Howells
  • James Pawson
  • Jeff Greenfield
  • Jeff Thomas
  • Jesse Frost
  • Jim Mitchell
  • jlr134
  • Joe Mastroianni
  • John Forcina
  • John Oberg
  • John Willcutt
  • Jon Newcomb
  • klugesmith
  • Leslie Wright
  • Lutz Hoffman
  • Mads Barnkob
  • Martin King
  • Mats Karlsson
  • Matt Gibson
  • Matthew Guidry
  • mbd
  • Michael D'Angelo
  • Mikkel
  • mileswaldron
  • mister_rf
  • Neil Foster
  • Nick de Smith
  • Nick Soroka
  • nicklenorp
  • Nik
  • Norman Stanley
  • Patrick Coleman
  • Paul Brodie
  • Paul Jordan
  • Paul Montgomery
  • Ped
  • Peter Krogen
  • Peter Terren
  • PhilGood
  • Richard Feldman
  • Robert Bush
  • Royce Bailey
  • Scott Fusare
  • Scott Newman
  • smiffy
  • Stella
  • Steven Busic
  • Steve Conner
  • Steve Jones
  • Steve Ward
  • Sulaiman
  • Thomas Coyle
  • Thomas A. Wallace
  • Thomas W
  • Timo
  • Torch
  • Ulf Jonsson
  • vasil
  • Vaxian
  • vladi mazzilli
  • wastehl
  • Weston
  • William Kim
  • William N.
  • William Stehl
  • Wesley Venis
The aforementioned have contributed financially to the continuing triumph of 4hv.org. They are deserving of my most heartfelt thanks.
Forums
4hv.org :: Forums :: High Voltage
« Previous topic | Next topic »   

HV transformer sc current measurements

1 2 
Move Thread LAN_403
Tom R.
Thu Oct 15 2009, 06:57PM Print
Tom R. Registered Member #2437 Joined: Thu Oct 15 2009, 05:58PM
Location:
Posts: 3
Hello group.

This is my first post, i'm just beginning with HV so please bear with me :)

I have a home built HV transformer of the following parameters:
input 230V, output around 10 kV
winding ratio is 500 on the primary side and around 23 000 on secondary giving a turn ratio of 46

Now i am wondering what are the max. currents on the primary and secondary side once the secondary is shorted.
How can i measure this safely without burning the ammeter and myself? :)

I'm thinking of applying 230V to the secondary terminals, then shorting the primary through an ammeter (since it will have only 5V) and simply rescaling the result obtained.

Is that proper thinking?
Back to top
Sulaiman
Thu Oct 15 2009, 07:06PM
Sulaiman Registered Member #162 Joined: Mon Feb 13 2006, 10:25AM
Location: United Kingdom
Posts: 3141
Please don't take this badly, I really want to help.
If you really are new to high voltage stuff - please do not make this transformer.
There are many ways to fail technically
If you succed the result will be lethal - start safer.
Back to top
Tom R.
Thu Oct 15 2009, 07:47PM
Tom R. Registered Member #2437 Joined: Thu Oct 15 2009, 05:58PM
Location:
Posts: 3
This transformer is already done, it has been tested and seems to operate correct drawing around 2-3 cm long arc.
I'm not taking any unnecessary risks.

Can you tell where did i make a mistake in my reasoning and how would you do it?
Back to top
Dr. Dark Current
Thu Oct 15 2009, 09:18PM
Dr. Dark Current Registered Member #152 Joined: Sun Feb 12 2006, 03:36PM
Location: Czech Rep.
Posts: 3384
I'd do it with a multimeter set to the 10(20) A range. Do you think your transformer puts out more than 10A? cheesey

Or you can do it like you said (run in reverse), but the s/c current calculated this way could be a little off (lower) than the real one.

Back to top
Sulaiman
Thu Oct 15 2009, 09:57PM
Sulaiman Registered Member #162 Joined: Mon Feb 13 2006, 10:25AM
Location: United Kingdom
Posts: 3141
Assuming that you've made a reasonably good transformer, the short circuit current can be assumed to be dominated by resistance and transformer action.
e.g 230 Vac to primary of 1 ohm, turns ratio 500:23,000 secondary resistance 2500ohms.
the primary resistance 'transformd' to the secondary is 1 x 46^2 = 2116 ohms
Added to the actual secondary resistance of 2500 ohms gives 4616 ohms effective.
So the output of your transformer behaves like 230 v 46 = 10500 volts rms
with a source resistance of 4616 ohms.
So the short circuit current should be 10500/4616 = 2.3 Amps rms.

The primary current should be 105.4 Arms - if a circuit breaker or fuse doesn't prevent it.
Back to top
Hazmatt_(The Underdog)
Fri Oct 16 2009, 07:06AM
Hazmatt_(The Underdog) Registered Member #135 Joined: Sat Feb 11 2006, 12:06AM
Location: Anywhere is fine
Posts: 1735
Here's some more info on transformers, hope this helps a bit: Link2
Back to top
Dr. Dark Current
Fri Oct 16 2009, 08:44AM
Dr. Dark Current Registered Member #152 Joined: Sun Feb 12 2006, 03:36PM
Location: Czech Rep.
Posts: 3384
Sulaiman: The leakage inductance often plays a big role too.

Back to top
Sulaiman
Sat Oct 17 2009, 06:53AM
Sulaiman Registered Member #162 Joined: Mon Feb 13 2006, 10:25AM
Location: United Kingdom
Posts: 3141
True, flux leakage will reduce the short-circuit secondary current,
but not enough to protect against overload, which was my main point - SAFETY.

Tom, you need a ballast, an inductor wold be most efficient, a mains lamp in series with the priary would be easy/cheap - or an electric heater element for more current etc.
Back to top
Steve Conner
Sat Oct 17 2009, 09:44AM
Steve Conner Registered Member #30 Joined: Fri Feb 03 2006, 10:52AM
Location: Glasgow, Scotland
Posts: 6706
Running the transformer backwards will kind of work. Here's what a commercial transformer maker will do:

The secondary winding is shorted, and a variable voltage is applied to the primary using a variac, through amp, volt and wattmeters. The voltage is carefully brought up from zero until the rated primary current is flowing, and the amount of voltage needed to flow this current is noted.

The impedance of the transformer can then be calculated by Ohm's law. Typically it's stated as a percentage. For instance, if your transformer has a 240V primary, and on the short-circuit test it only takes 12V to make rated current flow, then the transformer has an impedance of 5%.

This implies that if you apply 240V to the primary and short the secondary, then 100/5 = 20 times the rated current will flow. Bam!

If you don't have a variac, and don't know what the "rated" current of your transformer is because you made it yourself, you can't really do this, but you can still estimate what the short circuit current would be. Just do the calculations in ohms instead of percent.

A transformer maker would also do an open-circuit test, where he applies rated voltage to the primary with the secondary open, and measures the magnetizing current (on the ammeter) and core losses (on the wattmeter) On the short-circuit test, the wattmeter reads copper losses, so the transformer is now completely characterized by these two tests. The method really comes into it's own when you're making a 750MVA transformer but don't have a city to use as a dummy load. smile
Back to top
Antonio
Sat Oct 17 2009, 12:32PM
Antonio Registered Member #834 Joined: Tue Jun 12 2007, 10:57PM
Location: Brazil
Posts: 644
The scaled down measurement can be easily done with a lamp, or better, a linear resistor, in series with the primary coil. Measure the short-circuit secondary current and the primary voltage, that will be both low enough. Assuming that the transformer is linear (what is quite optimistic), the obtained transconductance will be valid with the normal input voltage too. Measure also the input impedance with the secondary coil open, with the same setup, and repeat both measurements with the transformer inverted. The four parameters obtained characterize completely a linear model of the transformer at the measurement frequency. The contributions of resistances and reactances can be obtained by looking at the phase differences between the signals in the measurements.
Back to top
1 2 

Moderator(s): Chris Russell, Noelle, Alex, Tesladownunder, Dave Marshall, Dave Billington, Bjørn, Steve Conner, Wolfram, Kizmo, Mads Barnkob

Go to:

Powered by e107 Forum System
 
Legal Information
This site is powered by e107, which is released under the GNU GPL License. All work on this site, except where otherwise noted, is licensed under a Creative Commons Attribution-ShareAlike 2.5 License. By submitting any information to this site, you agree that anything submitted will be so licensed. Please read our Disclaimer and Policies page for information on your rights and responsibilities regarding this site.