If you need assistance, please send an email to forum at 4hv dot org. To ensure your email is not marked as spam, please include the phrase "4hv help" in the subject line. You can also find assistance via IRC, at irc.shadowworld.net, room #hvcomm.
Support 4hv.org!
Donate:
4hv.org is hosted on a dedicated server. Unfortunately, this server costs and we rely on the help of site members to keep 4hv.org running. Please consider donating. We will place your name on the thanks list and you'll be helping to keep 4hv.org alive and free for everyone. Members whose names appear in red bold have donated recently. Green bold denotes those who have recently donated to keep the server carbon neutral.
Special Thanks To:
Aaron Holmes
Aaron Wheeler
Adam Horden
Alan Scrimgeour
Andre
Andrew Haynes
Anonymous000
asabase
Austin Weil
barney
Barry
Bert Hickman
Bill Kukowski
Blitzorn
Brandon Paradelas
Bruce Bowling
BubeeMike
Byong Park
Cesiumsponge
Chris F.
Chris Hooper
Corey Worthington
Derek Woodroffe
Dalus
Dan Strother
Daniel Davis
Daniel Uhrenholt
datasheetarchive
Dave Billington
Dave Marshall
David F.
Dennis Rogers
drelectrix
Dr. John Gudenas
Dr. Spark
E.TexasTesla
eastvoltresearch
Eirik Taylor
Erik Dyakov
Erlend^SE
Finn Hammer
Firebug24k
GalliumMan
Gary Peterson
George Slade
GhostNull
Gordon Mcknight
Graham Armitage
Grant
GreySoul
Henry H
IamSmooth
In memory of Leo Powning
Jacob Cash
James Howells
James Pawson
Jeff Greenfield
Jeff Thomas
Jesse Frost
Jim Mitchell
jlr134
Joe Mastroianni
John Forcina
John Oberg
John Willcutt
Jon Newcomb
klugesmith
Leslie Wright
Lutz Hoffman
Mads Barnkob
Martin King
Mats Karlsson
Matt Gibson
Matthew Guidry
mbd
Michael D'Angelo
Mikkel
mileswaldron
mister_rf
Neil Foster
Nick de Smith
Nick Soroka
nicklenorp
Nik
Norman Stanley
Patrick Coleman
Paul Brodie
Paul Jordan
Paul Montgomery
Ped
Peter Krogen
Peter Terren
PhilGood
Richard Feldman
Robert Bush
Royce Bailey
Scott Fusare
Scott Newman
smiffy
Stella
Steven Busic
Steve Conner
Steve Jones
Steve Ward
Sulaiman
Thomas Coyle
Thomas A. Wallace
Thomas W
Timo
Torch
Ulf Jonsson
vasil
Vaxian
vladi mazzilli
wastehl
Weston
William Kim
William N.
William Stehl
Wesley Venis
The aforementioned have contributed financially to the continuing triumph of 4hv.org. They are deserving of my most heartfelt thanks.
Registered Member #1025
Joined: Sun Sept 23 2007, 07:53PM
Location: Czech Rep.
Posts: 566
Harry wrote ...
Drying of transformer insulation using zeolite
That's great Harry! I have few kg of Zeolite, I was using it for removing water from ethanol few years ago... I'll give a try. Btw: Any chance to get the complete paper?
Registered Member #543
Joined: Tue Feb 20 2007, 04:26PM
Location: UK
Posts: 4992
Zeolite is an excellent molecular sieve, but I'm sorry I don't have access to the full paper. You'll need to ask someone with access to a university library system to get it for you.
Registered Member #56
Joined: Thu Feb 09 2006, 05:02AM
Location: Southern Califorina, USA
Posts: 2445
I am not sure about the legal implications of posting the article off ieee, but if you e-mail me (see profile) I can get it you. Just if anyone asks I totally thought that was my english paper.
Registered Member #543
Joined: Tue Feb 20 2007, 04:26PM
Location: UK
Posts: 4992
I have thought about your problem, Mates, and given the high value of your transformer if it can be salvaged would suggest the following approach.
1. Do not drain the oil below the level of the transformer, as your problems will be very much less if it can be salvaged without letting air into the windings.
2. Take a sample of the oil, and test with a colour-indicating dessicant. Use whatever means you have to determine (a) free water (b) emulsified water (c) water in solution.
3. Using a centrifuge if you have one, spin down a litre of the oil and examine for micro-particulates.
4. Test for the presence of colloidal metals and acetylene (indicative of arcing in oil) if you can.
5. Using a high voltage megohm meter measure the resistance between primary and secondary. If you do not have such a meter, then connect 10kV DC to the secondary and measure the leakage current into the primary. Good insulation shows a gradually climbing resistance over a period of five or ten minutes, but insulation contaminated by moisture will cause leakage currents sufficient to mask the dielectric absorption effect, and the leakage current will remain fairly constant (the so-called time-resistance insulation test)
6. If the winding is sound, and the water content is low, then I would suggest using cartridges filled with zeolite to desscicate the remaining oil in the transformer, so you will not be faced with the problem of air bubbles forming in the windings, and all the vacuum pumping needed to get rid of them.
Registered Member #1721
Joined: Sat Sept 27 2008, 08:44PM
Location:
Posts: 136
Hello:
Well it looks like you have your work cut out for you. Reference the H2O problem I would try the following after having first confirmed that you do not have huge amounts of H2O:
Most HV tanks like this seal very well, I would heat up the entire tank overnight to about 30-40C, with heating blankets, or a space heaters etc, in order to raise the vapor pressure of the H20. Then pull a vacuum on the tank with a refrigeration vacuum pump. This is what we did for large medical systems after removing all "visible" water. The pump was left on for up to a day depending on how bad it was.
If the oil is clear, to amber, with no free carbon, and you re-dry it as above it should be just fine. An old arc welder transformer makes a nice inductive current control unit if you are going to use it at a set KV/MA.
I would seriously consider selling/ trashing the tank, and going with a single phase one, or even using a second hand fluoroscopic HV unit to run your tube head instead, if these items are available in your area. -Or- Convert this one to run on single phase, leaving you with plenty of spare parts. This would simplify the control and "feeding" aspect of your project. At 1.5KW, single phase should be enough.
I would be interested at some point in seeing a picture of one of the XR tubes, then I can maybe help you with the cooling aspect, like if to use H20, or Vertrel XF cooling fluid etc.
Registered Member #1025
Joined: Sun Sept 23 2007, 07:53PM
Location: Czech Rep.
Posts: 566
Here are the promised pictures...
One of the six water cooled tubes I have. This one has Cr anode. The other anodes are Cu, Co,Ni, Fe.
This is the HV plugin together with HV switch removed form the oil tank... I want to make some maintanance on it
The holder of the tube is equiped by specialized filters from different materials...It has mechanical control unit for switching between the filters...
Registered Member #1134
Joined: Tue Nov 20 2007, 04:39PM
Location: Bonnie Scotland
Posts: 351
Those are X-ray Diffraction tubes. I have one myself, and ex-Russian tube rated for 24kV. Cooling is a walk in the park, since these are run with a grounded anode. the heated cathode is at, in your case -60kV
You can take advantage of the fact that those tubes have 4 Beryllium windows, thus emitting 4 beams, simultaneously.
Registered Member #1721
Joined: Sat Sept 27 2008, 08:44PM
Location:
Posts: 136
WoW :)
Nice collection of diffraction tubes, since the efficiency of x-ray production depends on the atomic number of the element, the higher the atomic number, the higher your output. In the case of the tubes that you have the Cu, and the Ni tubes are going to give you the highest, and hardest output, with the Cr tube being the lowest. When your input KV is well in excess of the K-edge line of the element, you will have a continous brems spectrum above the K-line also.
So in a nutshell: I would use the Cu tube, and keep the Ni as a backup to start with if you cannot locate one of the tubes below. A far better solution for your application would be to obtain a Mo, or W anode tube with a beryllium window. This would give you a far greater output, and far more penetration to achieve a much more uniform dose to your cultures. At the wavelength of your tubes even air absorbtion is a major factor, and dose uniformity, and even measurment will be a big problem.
Check around your area to see if you can get a Mo anode Mammography tube, these are now being changed out for Rhodium anode tubes, so many good tubes are available. Some of these come with oil cooling connections already in place. A second even better bet would be any large focal spot industrial tube, or a rotating Tungsten anode medical tube.
The absolute ideal for your application would be a CT scanner tube, these are rated in the Million heat units + range, and these are designed to be run at multi 10s of KW levels all day long!!! with oil / water cooling in a grounded anode configuration. They normaly change these out way before the tube is shot.
Running such a tube with your power supply is no problem, you could even put a voltage doubler circuit into the tank with a couple of caps for 120KV if you get a CT, or regular W anode medical tube, now you are cranking some serious rads. You can rotate the anodes in the medical tubes just fine with 110-220V and a 10-30mfd capacitor. I used a 100W mecury vapor lamp ballast to current limit the rotor circuit, and a capacitor to run the rotor in a grid controled tube I had.
If you get one and have trouble with the filament isolation voltage requirment with the higher KV Tungsten medical tubes, I may be able to help you out, with one that I have. To close I would seriously attempt to locate one of these tubes, its not as hard as you may think. Many medical tubes are changed because only one filament is open, or because the anode bearings are a little noisy. With a Mammography tube you will be able to use your existing filament transformer with a simple resistor etc. Also the operating values of these tubes is available on line easy, to help you set up your power supply.
Good luck, let me know if you ever want to get rid of the Fe, or Co anode tube, I do not have anything that soft in energy :)
Registered Member #1025
Joined: Sun Sept 23 2007, 07:53PM
Location: Czech Rep.
Posts: 566
Hello, Thanks a lot for your help guys. I have only few comments to your suggestions. There is a huge difference in designing a device which will be used in your home (private) conditions and in case it will be installed as part of University research facility. I mentioned in the beginning that the device will need an approval from the atom law authorities before is operated so all suggestion like DIY voltage doublers and incompatible tubes substitutions are out, despite are possible and would increased the performance. The photon distribution and problems with the energy of the light will have to be solved using a rotating platform (microwave oven based). I will stick to the heavier anodes for sure. Recently I run into interesting publications dedicated to the research of low energy (soft gamma) X-rays DNA damage induction and it really seems there will be no need for voltages over 60KV for my routine work. For special cases when hard gamma would be needed I have access to Cs and Co radioisotopes (the only problem is it that the sources are not in the same building as my lab is and its use is a bit restricted).
Small update of my work on the X-ray device: This weekend I cleaned the cables, all the mechanical switches and plug-ins (my hands look like I’m a car mechanic and not a scientist ). I redesigned the tube holder (all the filters are removed now and made the main window for the beam much bigger). I’m also designing the shielded box, I already ordered the lead and found a guy (company) who will make the box. Wish me good luck and I’ll keep you updated.
Registered Member #311
Joined: Sun Mar 12 2006, 08:28PM
Location:
Posts: 253
LutzH wrote ...
Most HV tanks like this seal very well, I would heat up the entire tank overnight to about 30-40C, with heating blankets, o
It would be more efficient & easier to use the windings as a heater. You can also determine internal temperature by measuring the change in resistance. Either use DC or short the secondary & current-limit the input to avoid any HV which might introduce breakdown.
This site is powered by e107, which is released under the GNU GPL License. All work on this site, except where otherwise noted, is licensed under a Creative Commons Attribution-ShareAlike 2.5 License. By submitting any information to this site, you agree that anything submitted will be so licensed. Please read our Disclaimer and Policies page for information on your rights and responsibilities regarding this site.