  • Guests: 70
  • Members: 1
Ian (37)
Lucas (40)
01/31 Mathias (42)
01/31 slash128v6 (53)
02/01 Barry (71)
Potential Transformers in series
kilovolt
Fri Oct 24 2014, 11:06AM Print
Dear highvoltage friends out there
recently I got the following two resin potted potential transformers for free from a power company:
6364
They have a turn ratio of 16'000V:100V each, but actually they are designed for 24kV permanent operation. At first I wanted to connect the high voltage windings in series for getting up to 48kV, but then I thought this might be a bad idea, because the potential against earth doubles as well, and there is always a capacitive coupling between earth and the high voltage winding, even though these are isolated transformers with two high voltage bushings. What do you think: Is it a risk to connect them at the high voltage side in series? Shall I better parallel them for double current output?
Thanks for your advice.
Best regards
kilovolt
hen918
Fri Oct 24 2014, 01:14PM
You are correct, there could be a risk of insulation failure, I would parallel them and use them along way away from anything remotely flammable, conductive or human!
Fri Oct 24 2014, 03:25PM
if in series, the high side one is likely to see secondary-to-primary insulation failure. im suspicious, they say 24kv contiouous use. but id worry with two beautiful transformers, you might kill one or both.
Fri Oct 24 2014, 03:50PM
I would suggest asking this guy: high1voltage1rules. Hes one of my friends and has a fair few PTs and good experiance with them...
Fri Oct 24 2014, 05:14PM
I am unsure how those are wound, but you can almost always get away with putting 2 transformers in series, so long as you ground the midpoint instead of one end. Then each transformer only sees its normal rated voltage, but the voltage measured end to end will be double.
Fri Oct 24 2014, 09:11PM
As long as it's mid-point grounded. Then it would be like a NST, but he said 48kv.
Sigurthr
Sat Oct 25 2014, 01:38AM
Midpoint ground them, too beautiful to risk destruction on.
kilovolt
Sat Oct 25 2014, 03:39PM
Hello All
Many thanks for your advices. I think, I will connect them only in parallel.
I'm not sure, if midpointgrounded is okay, because in normal operation, such a transformer is driven with floating highvoltage winding and if I'm right, this means half of the voltage on every terminal against earth (capacitive coupled). If one highvoltage terminal of every transformer is grounded, the other terminals have the full potential of one transformer against earth.
Thanks for your help.
Best regards
kilovolt
radiotech
Wed Oct 29 2014, 09:23AM
PTs are intended to operate at a standard burden on the LV to keep core flux at a level to
ensure accuracy.
Standard practice does see secondaries in series, however they are connected to
a constant voltage source limited to the nameplate voltage, with a BIL rating
perchance the line is hit by lightning.
Somewhere, there is a table, like the one below, to better describe how the
unit is wound, inductance wise.
PT secondary inductance is thousands of Henrys.
1414574630 2463 FT166808 Pt Burdens
kilovolt
Wed Oct 29 2014, 10:15AM
Hello radiotech
Thank you for your interesting answer.
Do you mean the configuration in a threephase grid on the high voltage side, right? I think this is another case, because, as you state as well, they are connected to a constant voltage which doesn't exceed the rated value of the transformer against earth potential. In my case, if I connect them in series, the voltage against earth is not defined.
Unfortunately I'm not able to interpret your table.
Best regards
kilovolt
