If you need assistance, please send an email to forum at 4hv dot org. To ensure your email is not marked as spam, please include the phrase "4hv help" in the subject line. You can also find assistance via IRC, at irc.shadowworld.net, room #hvcomm.
Support 4hv.org!
Donate:
4hv.org is hosted on a dedicated server. Unfortunately, this server costs and we rely on the help of site members to keep 4hv.org running. Please consider donating. We will place your name on the thanks list and you'll be helping to keep 4hv.org alive and free for everyone. Members whose names appear in red bold have donated recently. Green bold denotes those who have recently donated to keep the server carbon neutral.
Special Thanks To:
Aaron Holmes
Aaron Wheeler
Adam Horden
Alan Scrimgeour
Andre
Andrew Haynes
Anonymous000
asabase
Austin Weil
barney
Barry
Bert Hickman
Bill Kukowski
Blitzorn
Brandon Paradelas
Bruce Bowling
BubeeMike
Byong Park
Cesiumsponge
Chris F.
Chris Hooper
Corey Worthington
Derek Woodroffe
Dalus
Dan Strother
Daniel Davis
Daniel Uhrenholt
datasheetarchive
Dave Billington
Dave Marshall
David F.
Dennis Rogers
drelectrix
Dr. John Gudenas
Dr. Spark
E.TexasTesla
eastvoltresearch
Eirik Taylor
Erik Dyakov
Erlend^SE
Finn Hammer
Firebug24k
GalliumMan
Gary Peterson
George Slade
GhostNull
Gordon Mcknight
Graham Armitage
Grant
GreySoul
Henry H
IamSmooth
In memory of Leo Powning
Jacob Cash
James Howells
James Pawson
Jeff Greenfield
Jeff Thomas
Jesse Frost
Jim Mitchell
jlr134
Joe Mastroianni
John Forcina
John Oberg
John Willcutt
Jon Newcomb
klugesmith
Leslie Wright
Lutz Hoffman
Mads Barnkob
Martin King
Mats Karlsson
Matt Gibson
Matthew Guidry
mbd
Michael D'Angelo
Mikkel
mileswaldron
mister_rf
Neil Foster
Nick de Smith
Nick Soroka
nicklenorp
Nik
Norman Stanley
Patrick Coleman
Paul Brodie
Paul Jordan
Paul Montgomery
Ped
Peter Krogen
Peter Terren
PhilGood
Richard Feldman
Robert Bush
Royce Bailey
Scott Fusare
Scott Newman
smiffy
Stella
Steven Busic
Steve Conner
Steve Jones
Steve Ward
Sulaiman
Thomas Coyle
Thomas A. Wallace
Thomas W
Timo
Torch
Ulf Jonsson
vasil
Vaxian
vladi mazzilli
wastehl
Weston
William Kim
William N.
William Stehl
Wesley Venis
The aforementioned have contributed financially to the continuing triumph of 4hv.org. They are deserving of my most heartfelt thanks.
Registered Member #15
Joined: Thu Feb 02 2006, 01:11PM
Location:
Posts: 3068
Hello,
I've recently purchased several large 3-phase motors, and while doing testing, I'm find that the inrush current for these motors is about 180A for a duration of 100ms before settling down to about 60A which is the advertised datasheet inrush (lock rotor current) number.
I'm not an expert with motors, but is there typically an additional short term inrush (perhaps magnetizing current) for these motors thats above and beyond the typical inrush numbers which are advertised on the datasheet?
These are 440VAC, three phase motors and full load current is approx. 8A per phase, and locked rotor current of about 60A and advertised inrush of 63A.
But for every motor i've tested, i'm getting 180A PER PHASE for about 100ms on start-up. This current also occurs if the motor is just depowered for a second and is still rotating at a high speed.
Registered Member #2390
Joined: Sat Sept 26 2009, 02:04PM
Location: Milwaukee Wisconsin
Posts: 381
What is the horsepower of the motors? With that i can probably answer all of the questions. i Assume they are not squirrel cage type motors. The reason you still see the current for a short time after killing power is that you effectively have a generator at that point. The magnetizing current of your motors is typically less than 25% of their full load current. So it should be less than 2 amps / phase. If the motor is starting under heavy load the inrush will usually be higher than the advertised (no load) inrush. In industry, VFD's are usually used to control 3 phase motors, in addition line reactors are used to keep unwanted noise from feeding back into the line. VFD's use pulse width modulation and dc currents to accurately control the motor.
Registered Member #2099
Joined: Wed Apr 29 2009, 12:22AM
Location: Los Altos, California
Posts: 1716
Good mystery. It's hard to imagine conductor temperature accounting for more than 50% increase in cold start current, with respect to hot start current. And I never heard of three-phase motors with start windings or starter switches, centrifugal or thermal.
Can you reproduce the inordinate inrush current behavior in a single-phase induction motor? I bet they are found more frequently than three-phase induction motors in the labs of 4hv-ers.
Might the cause be like the occasional 10x inrush current in power transformers, which depend on inductance rather than back EMF to limit the current? Zero voltage is the -worst- phase to close the switch. To inductively buck the first half-cycle of voltage, we would need the normal peak-to-peak flux swing. Often impossible if flux starts at zero.
With little personal experience with three-phase motors, I wonder how much skew there is between three sets of switch contacts. How are you measuring the inrush currents? Can you record all three phase currents in a single start event?
Registered Member #103
Joined: Thu Feb 09 2006, 08:16PM
Location: Derby, UK
Posts: 845
Is the datasheet figure for inrush current based on 'star' rather than 'delta' configuration?
Induction motors in kit I've dealt with have a contactor to start the motor in star then switch to delta. As you're inrush current is about 3 times the rated, that implies 3 times the torque - which I think is also the difference in maximum torque between the star and delta configurations...
Registered Member #2099
Joined: Wed Apr 29 2009, 12:22AM
Location: Los Altos, California
Posts: 1716
New thing I learned today: Star Delta Starters. Thanks, Avalanche! One reference said they are being phased out (no pun intended) in favor of electronic soft starters.
Found this amusing exchange on a 3 phase forum thread. Q: A:
Registered Member #15
Joined: Thu Feb 02 2006, 01:11PM
Location:
Posts: 3068
The motor is a WEG W22 7.5hp motor.
It is wired for DELTA and powered with a DELTA 440VAC source. I wonder if this makes a difference vs. a star (wye) wired motor. As a delta wired motor as the full 440VAC voltage across each of the three windings whearas in a wye configuration, the voltage is distributed across two adjacent windings. And perhaps the advertised datasheet inrush current is actually for a wye motor.
Registered Member #2939
Joined: Fri Jun 25 2010, 04:25AM
Location:
Posts: 615
It has more to do with phase relationships in an R/L circuit. Normally if you drive an R/L circuit with a sine wave, and then plot V against I you get an ellipse centered on zero (its a circle for zero resistance), as V and I are out of phase. This is the "steady state" situation. On initial power up something else happens - at the start V and I are actually in phase, even though both are zero. Don't believe me? Ask yourself what the current is when V is zero in the steady state situation I first described - its definitely not zero! So somehow there is a transition from the initial state to the steady state, and this is where the inrush current surge comes from. It is most easily seen by plotting V against I for the initial few cycles. You can see the phasor plot shifted to one side, giving an initial current peak up to double the steady state value - see attached plot derived from a SPICE simulation.
It gets worse. In order to save weight and cost most motors and transformers have just enough iron to avoid saturation when running. The initial surge can easily saturate the iron, leading to a current peak several times that of the normal running condition.
Simulation of initial excitation of an R/L circuit :
It took me a while to get my head around this phenomenon when it was first explained to me.
Thinking about this some more this would be one reason why you'd start a motor in wye then switch to delta - as has been said, in wye connection the windings see a lower voltage, which would result in a lower inrush.
Registered Member #30
Joined: Fri Feb 03 2006, 10:52AM
Location: Glasgow, Scotland
Posts: 6706
What 2spoons said, the locked rotor current is a steady-state value. There is no back-EMF from a spinning rotor, but the magnetic circuit has got over its inrush and settled to a steady state.
I think of the initial transient as a "DC offset" because that's what it looks like when you plot current vs. time.
This source suggests an inrush current of >20x full load for the first half cycle, then 4-8x full load for several seconds until the rotor gets up to speed. That agrees with your measurements.
The advertised inrush current may have had some sort of marketing factor applied to it. Maybe they just mean that it won't pop a 63A Type-D breaker.
Registered Member #2390
Joined: Sat Sept 26 2009, 02:04PM
Location: Milwaukee Wisconsin
Posts: 381
Though the above answers are correct this doesn't happen very often. I talked to the resident genius engineer i work with and he believes you may have something else wrong. Can you post a snapshot of the nameplate on the motor? There are a few different connection options with that motor. Low and high, the genius informed me that if you feed the motor high voltage when it is wired for low or vice versa you will get exactly what you are seeing. He also said that there isn't a soft start or overload that could handle that type of inrush. You may be seeing the locked rotor current when the motor settles out because you have two windings wired so their fields are opposing. With no load on that motor you should not have a normal running current of 60 amps. here is a typical wiring scheme for a 460vac/480vac motor.
Tie together, 4&7 , 5&8 , 6&9 Connect the lines, L1 to 1 , L2 to 2 , and L3 to 3
This is for high voltage connection, not low. Also for WYE
How many leads are coming out of the box, aka "peckerhead"?? You may have it wired for delta when it should be wye or the opposite.
If it is rated 460 and you give it 440 you will also see a bit more current.
This site is powered by e107, which is released under the GNU GPL License. All work on this site, except where otherwise noted, is licensed under a Creative Commons Attribution-ShareAlike 2.5 License. By submitting any information to this site, you agree that anything submitted will be so licensed. Please read our Disclaimer and Policies page for information on your rights and responsibilities regarding this site.