I just got a High voltage plate transformer used for setting up the potential on the plate of a high voltage vacuum tube. It is rated to go about 1300v. I powered it up slowly with a variac while monitoring the current draw on the primary and the current and voltage on the secondary under various loads. It looks like it behaves like a MOT and I don't see any current limiting. The input current keeps going higher as I increase the variac.
I want to be safe when designing a transmission tube tester. I was planning to put a fast-blow fuse on the primary rated at a little more than the current I expect to draw. I want to protect the system from a shorted tube being inserted at the HV end. Any comments or suggestions from anyone?
|
Back to top
|
|
Sulaiman
|
|
Registered Member #162
Joined: Mon Feb 13 2006, 10:25AM
Location: United Kingdom
Posts: 3140
|
Assuming VARIAC - TRANSFORMER - RECTIFIER(S) - CAPACITOR as the setup;
My first choice would be a miniature circuit breaker (MCB) between Variac and Transformer.
A fast-blow fuse would be ok if you always 'wind up' the voltage from zero each test A sudden application of full ac voltage to the transformer would cause a large 'inrush current' that would blow the fuse. A slow-blow fuse would be ok but not as convenient as an MCB.